A colleague phoned me this morning saying she had turned her standard lamp on, on saturday, when she came back the light had gone off and 3 double sockets had stopped working.
She is terrified of electricty so I called over today, anyway on inspection the MCB had tripped, good news that the protective device was operating, however I removed the plugin MCB from the wylex CU (oldish looking)
Checked the rating and it was a 15A, I traced the circuit and I know it is a radial, supplying only these three double sockets.
Each socket had one of those "glade pluggin" things, she also had one standard lamp, and uses one double socket for hair straighteners and hair dryer.
All the connections appear to be sound (if somewhat messy), I haven't yet carried out Ins/res, continuity or polarity tests as I need to borrow a mates meter. (I'm still training)
Any how, because I know that the circuit is definitely a radial, should my first course of action be to replace the 15A MCB with a 20A MCB?
The MCB is BS3871 15A but has printed on the back 15/30A
Obviously I will carryout the neccessary tests, but looking for advice/opinion from the seasoned boys, cheers
She is terrified of electricty so I called over today, anyway on inspection the MCB had tripped, good news that the protective device was operating, however I removed the plugin MCB from the wylex CU (oldish looking)
Checked the rating and it was a 15A, I traced the circuit and I know it is a radial, supplying only these three double sockets.
Each socket had one of those "glade pluggin" things, she also had one standard lamp, and uses one double socket for hair straighteners and hair dryer.
All the connections appear to be sound (if somewhat messy), I haven't yet carried out Ins/res, continuity or polarity tests as I need to borrow a mates meter. (I'm still training)
Any how, because I know that the circuit is definitely a radial, should my first course of action be to replace the 15A MCB with a 20A MCB?
The MCB is BS3871 15A but has printed on the back 15/30A
Obviously I will carryout the neccessary tests, but looking for advice/opinion from the seasoned boys, cheers