Hi all,
hoping to get some help on an issue that has stumped me so far, builder mate has also had a look and not come to a conclusion. I’m new to plumbing issues and struggling to get my head round everything.
- Potterton Suprima HE 50 located on ground floor
- Hot water tank in airing cupboard directly above
- seperate F&E pipes leading up a tank in the attic
- 8 rad CH system, piping a mix of 22/15
System has had a few old rads and piping removed, optimised by using 21s instead of two 11s in two rooms, piping routed under floor boards, nothing major. Ran the system like this after the changes for a day and it worked fine, filled/bleed rads with no issues. I knew the pipes were dirty so then had a magnaclean filter fitted on the boiler return, plumber unfortunately balsed this up and leaked water into the PCB/cabling above it. I dried off all the electrics and he replaced the pcb. Boiler then ran for a short time before throwing up a circulation error code, plumber said the pump is not strong enough to push water through the system with the debris etc. the error shuts the boiler down for two mins and then it fires up again.
We agreed I’d run the MC3 for a week or so to see if it shifts the pump problem, I cleaned the filter multiple times over the next ten days and sure enough there is lots of debris on it. The circulation shutdown error happens consistently during this period, although if I run 4 rads only it seems to cope.
Pump was then changed as the problem kept happening, Grundfos UPS3. Pump running on slowest speed. Upon filling the system and running it with the new pump there seemed to be a ridiculous amount of air. Pump also sounds like it’s working against air/resistance which gets worse/louder on a higher speed. I also consistently had to bleed the HW vent and the few rads which were on. I wondered if air was entering via the vent.
System was drained today to fit an auto vent for the hot water, filled back up and bled, issue still happening. Builder mate thinks maybe heat exchanger is blocked up.
When I just put HW on the circuit is small an doesn’t seem to trip - boiler/HW/expansion towel rad, but there is still a ridiculous amount of air in it. The pump is audibly drawing water and maybe air, the auto vent is consistently venting, I can also consistently vent a small amount of air from the top of the towel rad, when I Ioosen the top magnaclean vent whilst everything is running it also releases air bubbles, almost consistently in sync with how the pump sounds when pushing. I’ve been in the attic and as the pump pulls the water level drops but then goes back up, the vent is also sucking, tried with a cup of water.
Could there be a blockage so pump sucks air via the vent which is then getting into the system? Is the boiler tripping because of the air or a blockage? I’ve check the thermistor readings and they are within tolerance and consistent with each other to 25%.
Anyone have any ideas????
Pic of the airing cupboard layout should hopefully be attached to this post. I believe the vent is directly below the pump and the feed goes into the HW return.
Thanks!
hoping to get some help on an issue that has stumped me so far, builder mate has also had a look and not come to a conclusion. I’m new to plumbing issues and struggling to get my head round everything.
- Potterton Suprima HE 50 located on ground floor
- Hot water tank in airing cupboard directly above
- seperate F&E pipes leading up a tank in the attic
- 8 rad CH system, piping a mix of 22/15
System has had a few old rads and piping removed, optimised by using 21s instead of two 11s in two rooms, piping routed under floor boards, nothing major. Ran the system like this after the changes for a day and it worked fine, filled/bleed rads with no issues. I knew the pipes were dirty so then had a magnaclean filter fitted on the boiler return, plumber unfortunately balsed this up and leaked water into the PCB/cabling above it. I dried off all the electrics and he replaced the pcb. Boiler then ran for a short time before throwing up a circulation error code, plumber said the pump is not strong enough to push water through the system with the debris etc. the error shuts the boiler down for two mins and then it fires up again.
We agreed I’d run the MC3 for a week or so to see if it shifts the pump problem, I cleaned the filter multiple times over the next ten days and sure enough there is lots of debris on it. The circulation shutdown error happens consistently during this period, although if I run 4 rads only it seems to cope.
Pump was then changed as the problem kept happening, Grundfos UPS3. Pump running on slowest speed. Upon filling the system and running it with the new pump there seemed to be a ridiculous amount of air. Pump also sounds like it’s working against air/resistance which gets worse/louder on a higher speed. I also consistently had to bleed the HW vent and the few rads which were on. I wondered if air was entering via the vent.
System was drained today to fit an auto vent for the hot water, filled back up and bled, issue still happening. Builder mate thinks maybe heat exchanger is blocked up.
When I just put HW on the circuit is small an doesn’t seem to trip - boiler/HW/expansion towel rad, but there is still a ridiculous amount of air in it. The pump is audibly drawing water and maybe air, the auto vent is consistently venting, I can also consistently vent a small amount of air from the top of the towel rad, when I Ioosen the top magnaclean vent whilst everything is running it also releases air bubbles, almost consistently in sync with how the pump sounds when pushing. I’ve been in the attic and as the pump pulls the water level drops but then goes back up, the vent is also sucking, tried with a cup of water.
Could there be a blockage so pump sucks air via the vent which is then getting into the system? Is the boiler tripping because of the air or a blockage? I’ve check the thermistor readings and they are within tolerance and consistent with each other to 25%.
Anyone have any ideas????
Pic of the airing cupboard layout should hopefully be attached to this post. I believe the vent is directly below the pump and the feed goes into the HW return.
Thanks!