Ive not long moved into a new house and the shower in the ensuite (Triton TS80i) every now and again trips after a few minutes.
After looking at previous posts it seems to be that my MCB is too small for the shower.
Am i right in saying that:
8.5kw > 36.9 amps = 40 amp MCB would be required??? It seems to be that there is only a 32a MCB fitted at present.
Am i ok to just change this though without knowing what size cables fitted to the shower?
If it makes any difference my consumer unit is relatively new as its a new build and the red breakers on the board are 100a and the RCD 80a.
I hope i have covered everything, hope someone can help