its not so much a case of current carrying capacity (6A is neither here nor there), but a case of keeping your Z's in spec, its going to have to be a C rated breaker, I'd go for a C10 and work from there, which gives you 1.92 ohms as your max Z's , which in all honesty shouldn't be that difficult to meet, whats the Z's at the distribution board this is going to be fed from?
C10 will easily handle the momentary 28A startup current drawn by the motor, and depending on the run length from the source and the ambient temperature of the environment, as well as other factors, 2.5mm T&E will be sufficient.