Where are all the cpcs?
I'm totally lost. I thought was that, quite apart from your 'local' issue of RCD tripping, the ongoing problem was very substantial currents flowing in the earthing conductors of yours and many other properties. Upgrading your CU and thereby replacing a (possibly) damaged RCD will surely not have made any difference to that. It may have cured your immediate problems (RCD tripping) but I would have thought it left the other, potentially worrying and dangerous, issue still there for you and your neighbours.IQA came out this morning, and had a hunch that the RCD, although testing OK, may have been mechanically damaged due to the amount of times it has been tripping.....
So, the pictures should speak for themselves, but two hours later, new split RCD board installed and NO TRIPPING!!!!! and I mean no tripping, not even any nuisance trips caused by any pre-existing problems that were unknown.
Kind Regards, John.
Good grief. All these alleged currents (in some cases several amps) flowing in earthing conductors is 'not right', and a sign of something unknown but potentially dangerous - at least, that's how it sounds to me!I fully agree with you. Yes it has stopped our immediate problems but in SP's opinion our "reported problem" (tripping/upstream tripping) is away so there is no need for further work.
I certainly think you should.Precisely, I think tbh, Scottish Power just wanted us to get off their backs hence the new CU, but if the problem is still there I will persist until it is sorted as it is a safety issue.
RCDs can become faulty for all sorts of reasons but, as I said, I can think of no sensible way that this could result in high currents flowing in the earthing conductor of your installation, let alone those of other properties! If it was so mechanically damaged that there were several amps flowing through the RCD's insulation to the earthed case of the CU, I would have expected there to be smoke and smell (if not flames) around to evidence that!Can you think of a reason why the new CU has stopped the tripping (could the RCD have been 'mechanically damaged')
I thought the g/y we can see would be earthing and bonding conductors.Looks like they're all there and bunched together.
I remain seriously confused. If this current is flowing when the DNO fuse in your installation is removed, I can but presume that it must be flowing between the incoming neutral and your main bonding (i.e. to incoming water pipe etc.) - I can't think of any other path available. .. and if the DNO fuse is removed, I'm not sure why 'turning things on' is making any difference. Am I missing something?Yes I couldn't understand it either, this current was just showing on a clamp meter, dno fuse out, clamped around the Earth wire after the meter. we even got this current to increase to 9 amps by turning on just about everything we could. (interestingly this also bumped our neighbours reading up by 2.5A - and to be clear this was the other neighbour, not our 'semi-attached' (there's a new word!) neighbour! SP said this is definitely the strangest case they have ever dealt with!