Went to a property today, the complaint was intermittent tripping of two lighting circuit mcb's with no obvious pattern.
The breaker was going with a heck of a bang, but there was no obvious noises out in the field, so to speak. There is no RCD on the circuit. The supply is single phase.
At exactly the same time, another breaker was popping. This other breaker was situated at the other end of the board, so I cannot blame thermal influences. I have also ruled out interlinking as there only needs to be one breaker off to isolate the circuit.
The fittings were removed (a mix of SELV d/l's & mains pendant fittings) and any joints and transformers examined. The dimmer module was taken OOC after a voltage check.
Here are the results. I have not had time (again!) to strip the circuit down & check IR yet. Monday's job.....:
L/N = 12V
Sw/N = 12V
Sw/E = Varies with dimmer
L/E = 400V.
I have three things that don't quite add up:
(i) the fact that two breakers pop.
(ii) The varying voltage.
(iii) the 400V reading.
The breaker was going with a heck of a bang, but there was no obvious noises out in the field, so to speak. There is no RCD on the circuit. The supply is single phase.
At exactly the same time, another breaker was popping. This other breaker was situated at the other end of the board, so I cannot blame thermal influences. I have also ruled out interlinking as there only needs to be one breaker off to isolate the circuit.
The fittings were removed (a mix of SELV d/l's & mains pendant fittings) and any joints and transformers examined. The dimmer module was taken OOC after a voltage check.
Here are the results. I have not had time (again!) to strip the circuit down & check IR yet. Monday's job.....:
L/N = 12V
Sw/N = 12V
Sw/E = Varies with dimmer
L/E = 400V.
I have three things that don't quite add up:
(i) the fact that two breakers pop.
(ii) The varying voltage.
(iii) the 400V reading.