Hi - first post here so hopefully I have done it right!
Hopefully someone can give me some tips or guidance with this one.
Basically have a 10 year old Ariston EuroCombi SX 20 Mffice boiler and all was working fine until I took two rads of the wall to decorate.
The rads valves were closed off and no leaks occurred during the two days they were off. the heating worked normally.
Put the rads back on, filled them and bleed the whole system to be sure.
Later that day heating stopped working and the system pressure was down to zero. Topped it up back to 1.5 bar as per Aristons manual. Within about 20 - 30 mins the pressure was back to zero.
First thing I did was check the two removed rads for leaks. All dry.
Next I suspected the expansion vessel. I had had this loose pressure a few years ago. An yes it was down to 5psi - should be about 15psi - 1 bar.
So today re-pressurised the expansion vessel with the system drained. And it seemed a bit better but still would not rise above 1.5 bar system pressure when running hot. Normally the system runs at 2.5 bar hot.
So today went out and got a new expansion vessel, fitted it and no difference. The system hold cold pressure at 1.5 bar for a while then slowly starts to fall off.
The system will just hold the 1.5 bar fill pressure, but does not rise up to
the normal 2.5 bar.
I have taken the front cover off the boiler and there is some scale around some of the joints but all are dry.
One last question - should the wet side of the expansion vessel be full of water. The old unit I took out was empty, but when I disconnected the pipe from the chw return there was water in it?
I guess I will have to leave it to go cold overnight to see what it really
does fall to, but before I call in a Corgi guy and have to pay top dollar is
there anything else I can test / check?
thanks for reading
EliTom
Hopefully someone can give me some tips or guidance with this one.
Basically have a 10 year old Ariston EuroCombi SX 20 Mffice boiler and all was working fine until I took two rads of the wall to decorate.
The rads valves were closed off and no leaks occurred during the two days they were off. the heating worked normally.
Put the rads back on, filled them and bleed the whole system to be sure.
Later that day heating stopped working and the system pressure was down to zero. Topped it up back to 1.5 bar as per Aristons manual. Within about 20 - 30 mins the pressure was back to zero.
First thing I did was check the two removed rads for leaks. All dry.
Next I suspected the expansion vessel. I had had this loose pressure a few years ago. An yes it was down to 5psi - should be about 15psi - 1 bar.
So today re-pressurised the expansion vessel with the system drained. And it seemed a bit better but still would not rise above 1.5 bar system pressure when running hot. Normally the system runs at 2.5 bar hot.
So today went out and got a new expansion vessel, fitted it and no difference. The system hold cold pressure at 1.5 bar for a while then slowly starts to fall off.
The system will just hold the 1.5 bar fill pressure, but does not rise up to
the normal 2.5 bar.
I have taken the front cover off the boiler and there is some scale around some of the joints but all are dry.
One last question - should the wet side of the expansion vessel be full of water. The old unit I took out was empty, but when I disconnected the pipe from the chw return there was water in it?
I guess I will have to leave it to go cold overnight to see what it really
does fall to, but before I call in a Corgi guy and have to pay top dollar is
there anything else I can test / check?
thanks for reading
EliTom