In a way but, perhaps not in actual numbers. A shed in the garden always raises these issues, whereas an attached garage does not.
If it's literally an 'attached' garage, then I would personal regard it as being part of the house (in some cases, that is obviously literally true), so I would not think of it any differently from any other 'rooms' in the house - i.e. earthing would be provided by the installation's CPCs in the usual way, and if any extraneous-c-ps enter the building through that 'room', they would be main bonded in the usual way.
There are those in another forum who just advocate TT for all such sheds - they just seem to like it. However, even they would not suggest it for the attached garage.
Indeed. I've dealt with e 'attached garage' above, but as far as TTing sheds in general, are they not perhaps considering issues
other than bonding? ....
Yes, agreed. Isn't that the only debate as far as the earthing arrangement of a shed? That is the cost of or difficulty of a suitable bond compared with installing TT.
As I've hinted, there are other issues, such as people standing (maybe with bare feet) on wet ground outside the shed and reaching in and touching an exposed-c-p (maybe a lighht switch, commonly just inside the door) - analogous with the 'outside tap' scenario. In many senses, that hazard is at its greatest when there are
no extraneous-c-ps in the shed to be bonded, since bonding, if present, will raise the potential of the nearby ground to closer to that of an exported TN-C-S earth which (very rarely) could be seriously elevated. Hence, some people (maybe bernard?) would favour always TTing outbuildings, even if (
particularly if) there was nothing in the outbuilding to bond.
Do you think anyone has ever "bothered" to satisfactorily resolve such a problem?
Well, "there's always one (or a handful)" but, in general, I agree that it's likely that very few people would 'bother' (even if they thought about it, which many probably wouldn't). However, it's all a bit ironical and inconsistent, since the same people who would not bother bonding (or even think about bonding) my daughter's kitchen floor which has been known to be covered with half an inch of mineral-rich water would quite probably be capable of getting 'emotional' about a few inches of unbonded extraneous-c-p (maybe an incoming metal water pipe, before it joined plastic plumbing) in some hardly accessible corner of the room!
Kind Regards, John