ASHP 22mm Pipe directly to std new radiator without stepping down to 15mm

It's a 4kw system with a water flow of usually around 12L/m. This flow reduces to 7.5L/m sometimes and as low as 5L/m on occasions.

The control unit says the temp difference between flow and return is about 5 degrees, it varies a little but no more than about 1/2 degree maybe a tad more on occasions.
You probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW
 
I'm confused - why would you have the heating on in the early hours of the morning?
It's cheaper to run by having an overnight setback of just a few degrees than having it controlled to to turn on and off at set times during the day.

Even over a weekend when i'm not at home it's cheaper to setback the temperature to 17 all day and night than have the heating off or controlled to turn on and off at preset times.

When the system was installed, the installer made it clear that the best way to use this ASHP system was to find a temperature i was happy with and leave it at that 24hrs a day. Explaining that it will be cheaper to run. The installer went on to say that if i set the system to turn on and off through the day it would take a long time to raise the temperature to the temperature i would want and it would cost more.

I have tried both approaches monitoring the performance and costs and they are correct. When turning off overnight the system takes hours to get back up to temperature and the same in the evening, it might get to temperature before i go to bed if i'm lucky!!!!!

However, leaving it on 24hrs it's getting far too warm for me in my bedroom, typically 21 degrees, sometimes as much as 24 degrees when its 19 in the living room. I want to turn this around in some way. I would be happier to turn the rad off altogether in my bedroom if i can find a way whilst at the same time increase the temp in the living room to 20/21. If i turn the room-stat up to 21 in the living room the bedroom temp gets to a very silly temperature!

When i try to gently restrict flow to upstairs rads (Reduce temperature upstairs) to move more water to the downstairs rads in the hope of pushing up the temperature a little (downstairs) i succeed to a point but not quite enough. If i push it too far the system switches off with water flow problems, flow too low. Noting when this happens i'm discovering that more often than not it's happening in the early hours and at the mo i'm assuming that it happens when the temperature drops to a point where the system turns itself back on again (or shortly afterwards after it's been running for a while) at a living room temp set at 17.

My gut feeling at the moment is to explore the idea of fitting a 2nd rad in the living room in the hope that i may be able to turn off the rad in my bedroom altogether or at least turn it down to a temperature that's ok (for me). 17/18 degrees!? The lower the better.

Now that the system is "Out Of Warranty" i feel that i can now do something myself without invalidating a warranty. The cost and process of fitting a 2nd rad in the living room is no big deal and if it doesn't workout i can either just turn it off or remove it.
 
You probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW
I didn't know this and i'll have a look at this and try to understand it and work out if it's somehow useful to me in some way. The info that the control unit gives me is limited and the level of control i have is limited too

Thank you
 
Thank you StephenStephen,

Interesting read and i've read several similar such articles over the last few years.

Having tried both options and having recorded how many daily KW/hrs the system was using, the costs and a measure of comfort in both scenarios and compared as best i can because weather (Outside temperatures etc) can vary month on month etc etc leaving the heating on with an overnight setback of 3 degrees did work out both significantly cheaper and more comfortable overall for me, for the system and the home where the ASHP system is installed. Numbers and costs on a spreadsheet prove it for me month on month when i recorded the data in the 1st winter of having the ASHP.

As Martin and others have always said, it can depend on all sorts of factors, "The Heating System", the weather, your own personal level of comfort expected, how well a home is insulated, and so much more.....................

Each system, people, home and level of comfort expected can vary enormously from home to home, each home being very different.

I've proved by recording and looking at the numbers and costs, taking into account an expected level of comfort that for me, my home and ASHP system that leaving it on with an overnight setback is much more economical and overall more comfortable throughout the whole day.

Other peoples systems, people, expectations and costs will no doubt vary enormously.

Again it's just those few short hours maybe three to four hours in a 24hr day when on an evening when the living room isn't quite warm enough and the bedroom is far too warm.
 
Any cheap IR thermometer from a DIY shop will do, so I wouldn't bother hiring one. It doesn't need to be accurate: it reads both ends of the radiator equally wrong, and the difference between them is what you're after. Just aim and read. A medical infrared thermometer (the forehead kind) is more precise, but you have to hold it right up to the pipe instead of aiming it from a distance.
The early hours are a useful clue. That's the coldest part of the night, when the heat pump defrosts its outdoor unit, and it does that by taking heat back out of the radiator water, so it needs its full water flow. With the bedroom valves throttled you're down to 7.5 or even 5 L/min, so my guess is the trips come with a defrost. If the control unit keeps an error log with times, see whether they line up. Johntheo5's sums show the other half: at 5 L/min your 4 kW unit can only put out under 2 kW, which is also why the living room lags.
So the aim is to keep the water moving at night:
Bedroom TRVs on max and the bedrooms set with the lockshields, so they don't close further as the rooms warm.
The living room TRV on max too: the room stat is in that room, and the two fight each other.
The second living room radiator is a good idea, and better than the conservatory if that's the room you want warm. Fit it without a TRV, or with the head on max, so there is always a wide-open path for the water at the far end of the run.
Ask at the December service for the filter to be cleaned.
A smaller setback, say 1-2 degrees, would make the morning restart gentler as well, but your spreadsheet says 3 degrees works for you, so try the flow changes first.
 