I'm confused - why would you have the heating on in the early hours of the morning?
You probably know this anyway from the display :It's a 4kw system with a water flow of usually around 12L/m. This flow reduces to 7.5L/m sometimes and as low as 5L/m on occasions.
The control unit says the temp difference between flow and return is about 5 degrees, it varies a little but no more than about 1/2 degree maybe a tad more on occasions.

It's cheaper to run by having an overnight setback of just a few degrees than having it controlled to to turn on and off at set times during the day.I'm confused - why would you have the heating on in the early hours of the morning?

I didn't know this and i'll have a look at this and try to understand it and work out if it's somehow useful to me in some way. The info that the control unit gives me is limited and the level of control i have is limited tooYou probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW