Awful Shower Installation.

Joined
11 Jan 2004
Messages
42,786
Reaction score
2,647
Country
United Kingdom
Hi guys! No piccys I'm afraid... :cry:

Right from the CU up...

6mm² T&E fed from 60A Wylex board via 32A MCB.

Tails undersized, PEB's undersized. No RCD. Cable not clipped and in contact with and wedged behind water pipes.
Cable not in safe zones and run under 200mm fibreglass insulation, switch in Zone 2 (burnt out big-time). No sleeving on cpc's. Circuit length approx 14m.

All this feeding a Galaxy 10.5kW shower.
 
Sponsored Links
postpics.gif
 
Just close your eyes and use the power of your fertile imagination!
 
Sponsored Links
Go on...try!!

Sully that millimetre-perfect, pristine mind of yours!!!
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top