• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Awful Shower Installation.

Joined
11 Jan 2004
Messages
45,845
Reaction score
3,514
Country
United Kingdom
Hi guys! No piccys I'm afraid... :cry:

Right from the CU up...

6mm² T&E fed from 60A Wylex board via 32A MCB.

Tails undersized, PEB's undersized. No RCD. Cable not clipped and in contact with and wedged behind water pipes.
Cable not in safe zones and run under 200mm fibreglass insulation, switch in Zone 2 (burnt out big-time). No sleeving on cpc's. Circuit length approx 14m.

All this feeding a Galaxy 10.5kW shower.
 
postpics.gif
 
Just close your eyes and use the power of your fertile imagination!
 
Go on...try!!

Sully that millimetre-perfect, pristine mind of yours!!!
 