Just check the following, some you may have already done but might be worth revisiting.
Flow and return valves fully open
All flow valves fully open
Pump set on max speed
Blending temp set at
You should see/get Flow return differentials of 7 degrees once the system
Has been running for about 6 hours if you have the thermostats demanding for heat.
If this doesn’t happen then it would suggest that either the floor sensor is positioned too close to flow pipe or faulty floor stat ( if this is causing that particular zone to be turned off or the floor is above 27)
Biggest problem we get with a mix of floor coverings is the heat output. Having too high an output on some floor coverings can cause those rooms to be much warmer and the air mixing through to other rooms creates a warm enough temp at 1.3m high ( but switches that zone off) creating the room to be too cold at seating height.
Flow and return valves fully open
All flow valves fully open
Pump set on max speed
Blending temp set at
You should see/get Flow return differentials of 7 degrees once the system
Has been running for about 6 hours if you have the thermostats demanding for heat.
If this doesn’t happen then it would suggest that either the floor sensor is positioned too close to flow pipe or faulty floor stat ( if this is causing that particular zone to be turned off or the floor is above 27)
Biggest problem we get with a mix of floor coverings is the heat output. Having too high an output on some floor coverings can cause those rooms to be much warmer and the air mixing through to other rooms creates a warm enough temp at 1.3m high ( but switches that zone off) creating the room to be too cold at seating height.