intermittent fault . ch and hot water but mostly dhw.boiler wont fire. micro switch on diverter is made.fan runs, pump runs.not sure if aps proves all the time.wondering if anyone has had similar fault.just tossing ideas around in my head until i go tomoz.
update. lasted a day and a half , problem back. seems that after the heating has reached temp it wont come back on until rads are near cool, but the water wont work either in this time.main heatx kettling.could it be the diaphram on the diverter , not the dhw diaphram the other one at back.everything was working when i was there.
Sounds like its had the overheat stat kit fitted and it still overheating?
Resets automatically when its cooled down.
Normal overheat problems tend to be associated with oversized (22mm) DHW pipework and dead legs (redundant DHW pipework) Example being if the boiler was put in, in place of a hot water cylinder.
update. again. called baxi to boiler as i could not get it not to work. They changed the thermister which was 4 days old. they fitted a new diaphragm in the diverter and fitted a new pcb.it now works .so i guess there was something a miss with the board.