Hi Guys,

I have a problem with my baxi combi 105e.

CH works fine but DHW does not recognise the hot tap being turned on. This happens in both CH/DHW and DHW only settings. Water may get up to luke warm and then run as cold as the mains cold.

DHW will heat the reserve tank to any temp set and I can get hot water by switching to DHW only and running the tap as system tries to heat the reserve tank.

Any ideas?

Mark
 
Sponsored Links
You have a 105 instant. HW Diaphragm has gone and needs replacing
 