Baxi Duo-Tec Combi - 'call for heat' light not coming on

Discussion in 'Plumbing and Central Heating' started by gw0udm, 26 Mar 2020.

  1. gw0udm

    gw0udm

    Joined:
    18 Feb 2016
    Messages:
    3
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi all

    I have a 7 year old Baxi Duo-Tec Combi boiler which is (naturally) just a couple of months out of warranty.

    The hot water is working fine, but the heating isn't coming on at all. It is definitely not the controls (which I have tested extensively) , and I have shorted out the thermostat terminals directly on the PCB but still nothing.

    The heating light on the boiler isn't coming on at all, and there are no error codes. It's as if it just isn't receiving the signal.

    I'm thinking it's the PCB on the basis that it's not even trying to fire up and it feels like an electrical issue rather than anything else. I can get a replacement off ebay fairly cheaply but would be really grateful for any thoughts of anything else I might be missing?

    Thanks very much

    James
     
  2. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,342
    Thanks Received:
    3,077
    Location:
    Daventry
    Country:
    United Kingdom
    Sounds like PCB to me but I wouldn't fit anything except a genuine, brand new in box one as a replacement. You don't know what's been done to these "refurbished" ones and whether they will affect the safe operation of your boiler
     
    • Thanks Thanks x 1
    • Like Like x 1
  3. Sponsored Links
  4. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    9,054
    Thanks Received:
    2,417
    Location:
    North
    Country:
    United Kingdom
    Yep, agree with @muggles, sounds like the pcb and wouldn’t buy secondhand or refurbed either. If you’re linking out the pcb end, then unless your selector is not on correct one, damaged, and the heating dial is up all the way, then wouldn’t really suspect anything else.
     
    • Thanks Thanks x 1
  5. gw0udm

    gw0udm

    Joined:
    18 Feb 2016
    Messages:
    3
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks very much both for the comments. I'm having to eat my words slightly in that after having another look at in the cold light of day I found that the problem was actually a seized up motorised valve which was leading to the boiler not being triggered properly. I don't know why I didn't realise this the day before but I was able to fix it by replacing the motor. So my boiler PCB lives to fight another day!

    Thanks again

    James
     
    • Thanks Thanks x 1
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page