Ignites, proves ignition but goes out shortly afterwards, switching thermisters to fool it, it stays on, measuring thermister both are within spec, replaced anyway proved thermister is not the fault. Can it now be anything but the control board?
Paul Barker said:Ignites, proves ignition but goes out shortly afterwards, switching thermisters to fool it, it stays on, measuring thermister both are within spec, replaced anyway proved thermister is not the fault. Can it now be anything but the control board?

Good advice to follow. If it's so, note that an occasional problem on Chaffoteaux Britonys (same as Baxi Genesis) is a partial blockage of the fan outlet venturi, which can result in the APS failing to switch, or switching back as pressure differential drops with warming as ChrisR described. The venturi is easily accessed if you first remove the fan. Blast some mains pressure water through all its tubes to clear any rubbish (I once had one blocked by a spider's egg nest!).ChrisR said:..run the thing with the corner of the cover loose, the APS will probably get a better pressure and the boiler keep going until you shut it.

poxi said:Baxi genesis
The biggest pile of s***te Baxi ever put there name to..

gazthepottertonengineer said:poxi said:Baxi genesis
The biggest pile of s***te Baxi ever put there name to..
I thought that was the Bahama![]()