Boiler not reaching thermostat temperature

Discussion in 'Plumbing and Central Heating' started by symbiosis, 11 Jan 2019.

  1. symbiosis

    symbiosis

    Joined:
    21 Jan 2017
    Messages:
    37
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi all

    I have a fairly ageing TURBOmax VUW 242 Vailent boiler.

    I Have my room thermostat set to 21 but just recently the boiler is cutting out at no more than 17. The rads are hot but the rooms are not!

    I have noticed that the pressure has creped up from a fairly steady 1.5 bar to just under 3 bar

    Any thoughts please?

    Thanks
     
  2. Sponsored Links
  3. KenGMac

    KenGMac

    Joined:
    24 Aug 2010
    Messages:
    2,856
    Thanks Received:
    496
    Location:
    Ayrshire
    Country:
    United Kingdom
    symbiosis, good evening.

    OK no answer to your pressure fluctuations.

    Can I suggest that you check the validity of the readings that the room stat is giving you, the Stat is set to "XXX" but is the Stat accurate?

    Ken
     
  4. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    3,893
    Thanks Received:
    783
    Country:
    United Kingdom
    Probably an expansion vessel problem causing the rise to 3 bar. What does pressure drop to when boiler is off ,and cooled down ?
    Raise the target temp on stat to 25 degrees and see what you get !!
     
  5. fixitflav

    fixitflav

    Joined:
    20 Mar 2018
    Messages:
    697
    Thanks Received:
    59
    Location:
    Stoke-on-Trent
    Country:
    United Kingdom
    I'd try turning the boiler control-stat up, see if that helps. There might be a high-pressure cut-out stopping it at 3 bar. The pressure problem needs sorting anyway, probably the vessel as terryplumb said.
     
    • Like Like x 1
  6. symbiosis

    symbiosis

    Joined:
    21 Jan 2017
    Messages:
    37
    Thanks Received:
    0
    Country:
    United Kingdom
    thanks for the replies, pressure goes to 2 bar when off (again much higher than before), was also wondering expansion vessel
     
  7. McCombi

    McCombi

    Joined:
    9 Jun 2012
    Messages:
    2,508
    Thanks Received:
    614
    Location:
    Aberdeenshire
    Country:
    United Kingdom
    Undersized rads for the rooms maybe?
     
    • Like Like x 1
  8. Sponsored Links
  9. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,013
    Thanks Received:
    2,777
    Location:
    Sussex
    Country:
    United Kingdom
    Filling loop valves on the T'max Plus are rubbish...there's every chance they are chewed up and allowing the system pressure to rise to mains pressure.
    The vessel will likely be low on charge or failed...needs looking at.
    Have you got the boiler heating thermostat turned up sufficient?
    If the radiator is kicking out heat at say 75 degrees (average across its surface) and the room is not reaching your target temperature it is too small for the rooms heat loss.
     
    • Like Like x 1
  10. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,315
    Thanks Received:
    876
    Country:
    United Kingdom
    If the radiators are boiling and the room is not warm enough then there's unlikely to be an issue with the boiler even if it is cutting in and out, it's just doing that to stop the system water overheating until the heat is lost from the radiators
     
    • Like Like x 1
  11. symbiosis

    symbiosis

    Joined:
    21 Jan 2017
    Messages:
    37
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for the replies, some more info:
    Boiler is shutting off at about 50 on its temp gauge
    Not had this issue previously and house has always been a toasty 21 even in the coldest of weather (its a bungalow so only 6 rads) so i thik can rule out undersized rads

    Would the pressure remain high (2 bar) when off if the pressure vessel needs priming or does that point to something else?
     
  12. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,013
    Thanks Received:
    2,777
    Location:
    Sussex
    Country:
    United Kingdom
    You should set the pressure to around 1 bar with the rads cold and the pressure should ideally not rise to more then 2 bar when red hot.
    Does the heating temp control on the boiler respond?
     
  13. McCombi

    McCombi

    Joined:
    9 Jun 2012
    Messages:
    2,508
    Thanks Received:
    614
    Location:
    Aberdeenshire
    Country:
    United Kingdom

    If it’s shutting off at 50 then turn stat higher on boiler
     
    • Like Like x 1
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page