boiler on lockout

Joined
3 Dec 2009
Messages
2
Reaction score
0
Location
Anglesey
Country
United Kingdom
hey guys, i have a heatslave 15/19 and i ran out of oil yesterday due to delivery being late. oil delivered today and after i restet the lockout indicator button at the bottom it fires up for a minute or so and then goes back to lockout. any help?
 
Sponsored Links
I reckon you have air in the oil line that needs removing by bleeding.
Should be easy if the oil level in tank is higher than pump.
 
Sponsored Links
Turn the tank valve off
Undo the flexible pipe connection where it enters the burner pump
Turn tank valve on
Collect air free oil into a container
Turn the tank valve off and reconnect at the burner
Turn the tank valve on and press the lock out light on the controller. The pump should self bleed....and obviously having a mate helps here!