Couple of interesting things to report:
First I took a look at the valves (which, incidentally, are Lifestyle 679H308-30L1 ).
Both are mounted upside down.
Powered off.
The left one - the black lever very easily moves, no resistance at all. I put it back to its original position after this.
The right one - the black lever encounters fairly heavy resistance - it's not stuck, it just feels like pushing against motor resistance as it will very slowly move. I put it back to its original position after this.
After doing the above I powered back on - the right lever moved a little (resetting itself I guess but was still roughly in the same original position) but the left didn't move on its own.
The water continued to make its usual sounds in the pipes, some very slight humming from the pump, etc.
So as I have a spare, new, TF830.3 control box I thought I'd change that, just to rule it out.
Powered back on and no noise from the pipes ........... (great!).
Tested the boiler, fired it up for half an hour, all working okay, then back off.
Still no noise from the pipes - even better!
I'm hesitant to call it fixed at this early stage, but currently replacing the control box appears to have stopped the water noise from the pipes, no pump hum either. More testing required of course.
One proviso:
I still don't know the cause the the high-ish pitch vibration that I briefly heard a few times late yesterday. Perhaps something in the valves or pump rapidly clicking on/off due to a control box fault? I still slightly suspect the valves or the pump are the cause of that (so not down to control box issues, instead mechanical problems) but we'll see.
Thanks a lot for all of your excellent help so far!
First I took a look at the valves (which, incidentally, are Lifestyle 679H308-30L1 ).
Both are mounted upside down.
Powered off.
The left one - the black lever very easily moves, no resistance at all. I put it back to its original position after this.
The right one - the black lever encounters fairly heavy resistance - it's not stuck, it just feels like pushing against motor resistance as it will very slowly move. I put it back to its original position after this.
After doing the above I powered back on - the right lever moved a little (resetting itself I guess but was still roughly in the same original position) but the left didn't move on its own.
The water continued to make its usual sounds in the pipes, some very slight humming from the pump, etc.
So as I have a spare, new, TF830.3 control box I thought I'd change that, just to rule it out.
Powered back on and no noise from the pipes ........... (great!).
Tested the boiler, fired it up for half an hour, all working okay, then back off.
Still no noise from the pipes - even better!
I'm hesitant to call it fixed at this early stage, but currently replacing the control box appears to have stopped the water noise from the pipes, no pump hum either. More testing required of course.
One proviso:
I still don't know the cause the the high-ish pitch vibration that I briefly heard a few times late yesterday. Perhaps something in the valves or pump rapidly clicking on/off due to a control box fault? I still slightly suspect the valves or the pump are the cause of that (so not down to control box issues, instead mechanical problems) but we'll see.
Thanks a lot for all of your excellent help so far!