Boilermate 2000 issue

Joined
3 Dec 2015
Messages
2
Reaction score
0
Country
United Kingdom
My Boilermate 2000 shows all 3 red bars and 3 green LEDs on but we have no central heating and hot water. The header tank is full. The boiler works fine albeit no signal to switch on appears to be received from the Boilermate 2000. All 3 pumps appear fine but do not switch on. Thermostat for central heating clicks on/off when adjusted. Any ideas?
 
Sponsored Links
Is there not an overheat reset you can do?

May be engineer only though.

Do you ever have it serviced?

Tony
 
What boiler do you have heating the Boilermate? It may well be an issue. There's very little to "service" on a Boilermate.
The PCB's and sensors are fragile on these.
 
Sponsored Links
Contacted a local heating engineer. He thought it could be the PCB andcontacted Glehill who confirmed his diagnosis. Hope to have the PCB replaced tomorrow.
 