• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Boilermate 2000 issue

Joined
3 Dec 2015
Messages
2
Reaction score
0
Country
United Kingdom
My Boilermate 2000 shows all 3 red bars and 3 green LEDs on but we have no central heating and hot water. The header tank is full. The boiler works fine albeit no signal to switch on appears to be received from the Boilermate 2000. All 3 pumps appear fine but do not switch on. Thermostat for central heating clicks on/off when adjusted. Any ideas?
 
Is there not an overheat reset you can do?

May be engineer only though.

Do you ever have it serviced?

Tony
 
What boiler do you have heating the Boilermate? It may well be an issue. There's very little to "service" on a Boilermate.
The PCB's and sensors are fragile on these.
 
Contacted a local heating engineer. He thought it could be the PCB andcontacted Glehill who confirmed his diagnosis. Hope to have the PCB replaced tomorrow.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top