hi lads, whats the minimum flushing req.to comply to bs.7593 for benchmark? boss says just bung it on the wall
 
perdona.gif
 
obviously thats not what i intend to do,but i can't find any definition of the standard
 
thanks kev, i tried that site first but can't get any info out of it.just wondered what the best practice is for boiler changes
 
bs=below standard.

who is going to check it afterwards.no one..
if system is old,it wont all clean out so you just do your best and record details of old system on paper work.
new system.flush out with mains water before connecting boiler.then flush out with commisioning cleanser.flush again then add inhibitor.
then test sample of water with senintal test kit and record this detail on paper work.get house holder to witness this test.
 
phone the technical service line of the boiler manufacturer.