C/H Bonding

Joined
30 Jun 2004
Messages
661
Reaction score
57
Country
United Kingdom
1. the boiler is cross bonded
2. the bathroom rad is suppl. bonded.
3. the incoming gas and water are bonded in to the MET.
Is this how it should be - and leave well alone? Or should some re-arrangeing take place?
 
There should be supp bonding in the bathroom between H & C.
If you have an electric shower fitted, there should be a bond from cpc connection to water pipe.
And a connection from shower cpc in switch to ceiling rose.
 
Posted same earlier


All things connected together, in one continuous cable (min 4mm sq without mechanical protection)

from rad to all pipes then to bath, shower and lighting circuit- do not bond SELV (12 V lights) but DO bond supply to those, if in zones.

A bit fron the IEE on site guide, it's quite handy

http://www.baldelectrician.com/bathroomtemp.jpg
 
thank you both for the info. but the IEE diagram doesnt show continuous bonding in a single 4mm?
 
The diagram is using the continuity of the plumbing.

THINK!
Equipotential Bonding is to have ALL exposed conductive parts at the same potential so that if a fault occurs and something becomes live (even for a fraction of a second) there will be no potential difference between that and another exposed condutive part. Wet bodies conduct electricity!!
 
i originally asked the question to determine if the boiler cross-bonding was redundant and to tease out any anomalies. The IEE diagram still doesn't show continuous 4mm supp. bonding.
 
tim00 said:
i originally asked the question to determine if the boiler cross-bonding was redundant and to tease out any anomalies.
The boiler is probably cross bonded for continuity between pipes, i.e. where they enter the boiler they may not have a brilliant electrical cross connection and for safety, cross bonding has been installed. The cross bonding has been installed for a reason and should be treated as a "Safety Electrical Connection - Do Not Remove."
The IEE diagram still doesn't show continuous 4mm supp. bonding.
It doesn't need to be a continuous length of 4mm² cable, the copper body of the pipework can be used as a conductor.
 