In other recent and current threads, there has been a lot of discussion about what (if any) codes should be given on an EICR for things which were compliant when installed, but not compliant with current regs, and even what (if any) code should be given to things which were not compliant when installed, but are not judged to present significant danger.
BS7671 itself now says very little about EICRs (and, indeed, never uses that term), Chapter 65 ("Periodic Inspection and Testing") now consisting of little more than one page. However, there is a fair bit more said in the guidance of ('informative') Appendix 6 in the context of notes and guidances for those undertaking EICRs. This includes (my red highlighting) ...
This seems to be indicating that a non-compliance should not be reported (hence coded) if it is not consiered that it "may give rise to danger" - and, indeed, if one takes that second sentence in isolation (which I suspect is the intention), that would remain the case even if the situation in question had not been compliant with regs, even when installed.
Of course, if one scrapes the barrel deeply enough, it can probably always be argued that anything to do with electricity "may give rise to danger" so I would think that the common sense (and probably 'intended') interpretation is that they are talking about "significant danger" (which is, of course, a subjective judgement in a good few cases).
Their apparent intention that some non-compliances with current regs should not be given any code (if it is judged that they don't present a 'significant danger') seems to be reinforced/confirmed by what seems to be the one and only place where they say that a particular (minimum) code should be given for a particular non-compliance, namely ...
The implication of that statement is presumably an acknowledgement of the fact that, without it, it would have been possible for someone not to give any code for the absence of RCD protection.
Of course, being in an 'informative' Appendix, none of the above is more than 'guidance' (not that compliance even with BS7671 itself is 'mandatory').
Kind Regards, John
Appendix 6 of BS7671:2018 said:CONDITION REPORT
Notes for the person producing the Report:
1 ..... An installation which was designed to an earlier edition of the Regulations and which does not fully comply with the current edition is not necessarily unsafe for continued use, or requires upgrading. Only damage, deterioration, defects, dangerous conditions and non-compliance with the requirements of the Regulations, which may give rise to danger, should be recorded.
Appendix 6 of BS7671:2018 said:CONDITION REPORT INSPECTION SCHEDULE
GUIDANCE FOR THE INSPECTOR
..... 2 Older installations designed prior to BS 7671:2018 may not have been provided with RCDs for additional protection. The absence of such protection should as a minimum be given a code C3 classification (item 5.12).
Kind Regards, John