Cable size for 6kw hob
26 Jan 2006
Aberdeen
Hello again guys, need some more advice. Fitting a 6kw ceramic hob above a 2.3 kw oven (which now has its own dedicated 2.5mm radial circut to the new consumer unit). Was planning to use existing 6mm cable for the hob. What meagre instructions there are recommends the hob should be connected with 2.5mm heat resistant which is fine but where do I connect it to the 6mm ? Do I run the 2.5mm to the cooker outlet and then to the load terminals on the cooker switch therefore avoiding putting 6mm and 2.5mm in the same terminals on the cooker outlet or does it matter? My other problem is the electrician who installed the consumer unit says he had to attach a 40amp breaker to the hob radial because the 6mm cable requires it. That seems to me to be far to big considering there is 2.5mm cable down the line. Do I replace the breaker with a smaller one and what size? Hope I'm making myself clear and any help would be much appreciated.
Would advise 4mm² heat resistant flex, no problems with connecting it to the cooker connection point, each terminal is like two terminals on one piece of copper if that makes sense, so it doesn't matter that the cables are different, swap breaker for a B32