No, obviously I meant no restriction - reduction - on the maximum CCC of a particular cable.I presume that your tongue in in your cheek, and that you're not suggesting that (because of this omission in the regs), it would be OK to wire my 10.5 kW shower with 1mm² cable, provided the cable ran entirely in an uninsulated stud wall
Yes, but if the basic tabulated CCC of a cable is, say, 27A then do or can the regulations list every circumstance that does not reduce that CCC?... or (looking at your last two quotes above) are we perhaps talking at cross-purposes? As I presume you understand, the reason I would like to know the Reference Method for installation of a cable in an uninsulated stud wall is obviously in order that I can look up the 'basic tabulated CCC' for a particular cable, before applying any 'restrictions' or 'de-rating factors'
Perhaps we need a better definition of 'free air'.