Cables in Timber frame extension

Radial circuit 4.0mm cable on 20A MCB, run in conduit.
That would obvioulsy be fine if the OP (and his electrician) regarded 20A as being adequate for the likely maximum load on his 6 double sockets. If not, then the alternative would be a ring final circuit with 4mm² cable on a 32A MCB, run in conduit.

Kind Regards, John.
 