Final circuits for sockets are;
A1 Ring, 30 or 32 amp overcurrent device, minimum cable size 2.5 mm2.
A2 Radial, 30 or 32 amp overcurrent device, minimum cable size 4 mm2.
A3 Radial, 20 amp overcurrent device, minimum cable size 2.5 mm2.
Therefore, you would (I assume) be simply extending the shower cable and keep it as a radial, A2 or A3.
If you extend the circuit in 4 or 6 mm2, fit a 30 or 32 amp in place of the 40 amp.
You may well prefer to extend the circuit in 2.5 mm2 cable, as it's cheaper and easier to work with. In this case fit a 20 amp in place of the 40 amp.