can I run sockets off unused 6mm Shower cable?

Joined
20 Apr 2012
Messages
1
Reaction score
0
Location
West Midlands
Country
United Kingdom
Hello, I Have 6mm shower cable running through spare room, this is connected to 40amp breaker. My shower now runs off boiler so could I run a spur off this? Thanks.
 
Sponsored Links
Final circuits for sockets are;

A1 Ring, 30 or 32 amp overcurrent device, minimum cable size 2.5 mm2.

A2 Radial, 30 or 32 amp overcurrent device, minimum cable size 4 mm2.

A3 Radial, 20 amp overcurrent device, minimum cable size 2.5 mm2.

Therefore, you would (I assume) be simply extending the shower cable and keep it as a radial, A2 or A3.

If you extend the circuit in 4 or 6 mm2, fit a 30 or 32 amp in place of the 40 amp.

You may well prefer to extend the circuit in 2.5 mm2 cable, as it's cheaper and easier to work with. In this case fit a 20 amp in place of the 40 amp.
 
Sponsored Links
What are you planning to spur off from this 6mm cable?
 