I've just been doing some testing on a couple of caravans.
Not my field but thought it might be interesting.
But my findings where quite scary, I wont pretend it's my forte and I do believe they are governed by more by a BSEN that I can't get my hands on.
But my findings are as follows.
1, More than One circuit protected by a single breaker,
2, ELV and LV cables being run and grouped together,
3, CU pop riveted, so no means of access.
4, Neon indicator on CU which could not be disconnected because of above
5, All circuits joined by snap on and pull off connectors under beds, in cupboards etc...
6, Cables run in polystyrene
7, A spurred socket wired in speaker wire
8, No means of testing the fridge circuit as the fridge is a fixed appliance and can not be moved.
9, No earth bonding connection to chassis (this is a requirement)
10, Curtains drapes dangerously close to light fittings
Some of the findings prevented me from carry out tests such as IR due neon light in unaccessible CU.
This caravan had been in for service ready for a resale and actually had been bought be someone.
It's my understanding that caravan electrical servicing only include the RCD test and the plug in tester that indicates earth connection and polarity.
They don't do PIRs,
and the people who design and install them should be on the shooting list, in fact I'm going post that.
Not my field but thought it might be interesting.
But my findings where quite scary, I wont pretend it's my forte and I do believe they are governed by more by a BSEN that I can't get my hands on.
But my findings are as follows.
1, More than One circuit protected by a single breaker,
2, ELV and LV cables being run and grouped together,
3, CU pop riveted, so no means of access.
4, Neon indicator on CU which could not be disconnected because of above
5, All circuits joined by snap on and pull off connectors under beds, in cupboards etc...
6, Cables run in polystyrene
7, A spurred socket wired in speaker wire
8, No means of testing the fridge circuit as the fridge is a fixed appliance and can not be moved.
9, No earth bonding connection to chassis (this is a requirement)
10, Curtains drapes dangerously close to light fittings
Some of the findings prevented me from carry out tests such as IR due neon light in unaccessible CU.
This caravan had been in for service ready for a resale and actually had been bought be someone.
It's my understanding that caravan electrical servicing only include the RCD test and the plug in tester that indicates earth connection and polarity.
They don't do PIRs,
and the people who design and install them should be on the shooting list, in fact I'm going post that.