Central heating not working

Joined
12 Oct 2014
Messages
6
Reaction score
0
Location
Northamptonshire
Country
United Kingdom
I'm trying to diagnose a problem with my friend's CH.

It is a conventional gravity fed system, controlled with a Honeywell ST9400 programmer in conjunction with a HCW 80 room thermostat and HC60NG relay module.

The hot water side of things works normally.

I've performed the "teach in" between the room stat and the relay module several times, the green led operates on the module when the room stat is triggered. I can hear the relay operate in the module but almost immediately it sounds like it has switched itself off.

I have checked the three port valve by moving the slider to the end of it's travel, it only appears to go half way back? If I hold the slider in it's fullest position, when I operate the room stat the pump will also only work momentarily with the relay switching on and off.

Could the problem be the three port valve?

Thanks

John
 
Do you have the means for safe electrical testing?
 
check for mains power on the white wire to the valve, when there is a call for heating .
 
No feed to the white wire.

It is fed momentarily when relay cuts in and then out.

By linking a 240v feed directly to the white wire it operates the valve, so from that I assume it's the room stat or the relay module or both!
 