Changing to MCB's, why a bigger rating?

Joined
7 Jun 2008
Messages
128
Reaction score
0
Country
United Kingdom
When circuits are updated, why are the circuits increased in rating.

30amp fuse >32amp breaker
5amp fuse > 6amp breaker
15amp fuse > 16amp breaker

Surely this has now given the cable more chance to heat up in the event of a fault?
 
Sponsored Links
newboy wrote

Surely this has now given the cable more chance to heat up in the event of a fault?

not really because you will still calc the circuit out so that you confirm the OPD will do all it needs to.
 
Using existing circuit cables the lights (5amp) has now been allowed an extra 20% to 6amp on the mcb.
Granted the mcb has a faster reaction time with high current.
 
The opposite it true, the MCB is slower than a fuse at high current! Generally a fuse pops quicker as the current increases, MCBs steady out as they are mechanical.
As industryspark says though, the calculations should be done for the circuits to ensure the overcurrent protective device correctly protects the cable.
You normally need to ensure protection against overload current and fault current.
An MCB has 2 parts, magnetic and thermal. The thermal part deals with overload current and magnetic part deals with fault current.
The thermal part of an MCB normally has a fusing factor of 1.45. Rewireable fuses have a fusing factor of 2, this means it takes a bit more overload current to disconnect a 30A rewireable fuse than a 32A MCB.
Fault current wise the circuit in either case should rapidly disconnect which is why we need to design them properly and inspect/test them to ensure they comply!
 
Sponsored Links
The basic answer is:

Fuses don't actually blow at their rated current, it takes more, say 8+ amps for a 5 amp fuse. MCB's don't trip at their rated current either, say 8+ amps for a 6 amp MCB. So the 5amp fuse - 6amp MCB is comparable in the amount of current they will need to blow/trip. Same goes for 15/16, 30/32 . . .
 