choice of mcb type and ka??
8 Jun 2008
Bristol
hi guys,
i am trying to select the best mcb and rcbo's for my new cu. wylex 15 way split load, dual rcd, high integrity
3 x lights 6 Amp type c 1.5mm t&e
2 x socket 32 Amp type b 2.5mm t&e
1 x fridge 16 amp type b rcbo 2.5mm t&e
1 x loft socket 16 amp type b 2.5mm t&e
1 x shower 50 Amp type b 10mm t&e
1 x cooker 32 amp type b 10mm t&e
1 x alarm 6Amp type b
1 x door bell 6Amp type b
1 x outside flood lighting 6Amp type b 1.5 t&e
1 x garage sockets and lights 16 amp type b 2.5 swa
but the question is 10ka or 6kA mcb's , can anyone explain the difference?
any suggestions about the choices, feel free to comment
:D
You'll need to measure PFC (highest reading from PEFC and PSSC) to know for sure but 6kA will probably be fine for a domestic CU.
PFC - prospective fault current, the maximum current that will flow under earth fault or short-circuit conditions. Your chosen protective device must be capable of breaking this fault current without damaging the protective device in the process.
It depends on you incomming earth and fault loop and neutral impedence.
This can be used to work out the maximum current which will flow in the event of a fault. The MCBs must be rated to at least this value.
Usually 6kA will be sufficient for a domestic supply, but not always.
10kA will somtimes not be enough for some commercial / industrial supplies, but it is unlikely to find a domestic supply which is >10kA
Where a service cut-out contains a BS1361 type 2 fuse and supplies a consumer unit to BS 5486-13 or BS EN 60439-3 (modern CU) then the short circuit capacity of the overcurrent protective devices in the consumer unit may be taken to be 16kA.