hi guys,
i am trying to select the best mcb and rcbo's for my new cu. wylex 15 way split load, dual rcd, high integrity
3 x lights 6 Amp type c 1.5mm t&e
2 x socket 32 Amp type b 2.5mm t&e
1 x fridge 16 amp type b rcbo 2.5mm t&e
1 x loft socket 16 amp type b 2.5mm t&e
1 x shower 50 Amp type b 10mm t&e
1 x cooker 32 amp type b 10mm t&e
1 x alarm 6Amp type b
1 x door bell 6Amp type b
1 x outside flood lighting 6Amp type b 1.5 t&e
1 x garage sockets and lights 16 amp type b 2.5 swa
but the question is 10ka or 6kA mcb's , can anyone explain the difference?
any suggestions about the choices, feel free to comment