Combi boiler, drain heating & use hot water

Joined
15 Jun 2004
Messages
7,403
Reaction score
334
Location
Norwich
Country
United Kingdom
I need to remove an upstairs radiator, can i drain system, remove the radiator & leave the boiler for hot water only. Boiler switched to water only, programer turned to heat off.
 
You can't drain the boiler ,it would have to retain water inside it. You would need to close its flow and return isolation valves before draining heating system.
 
so are you altering the pipework to upstairs rad ?
 
so are you altering the pipework to upstairs rad ?
No, I want to take a towel rail off so I can decorate.
I was thinking if the room stat was calling for heat, then the valve would be closed so that I could demand hot water
 
No, I want to take a towel rail off so I can decorate.
I was thinking if the room stat was calling for heat, then the valve would be closed so that I could demand hot water
just close the towel rads valves and remove that will leave water in system so the hot water works with no need to touch boiler valves which are notorious for leaking when touched
 
just close the towel rads valves and remove that will leave water in system so the hot water works with no need to touch boiler valves which are notorious for leaking when touched
Ok thanks. BTW Boiler is Greenstar Highflow 440
 
No, I want to take a towel rail off so I can decorate.
I was thinking if the room stat was calling for heat, then the valve would be closed so that I could demand hot water
If you isolate one rad you can leave the HW and CH working as normal. The other rads are still working. You'll need to repressurise when you refit the rad and bleed it as it refills.
But why bother removing the rad? It's usually possible to paint or wallpaper behind a rad so the bits missed aren't readily visible.
 
If you isolate one rad you can leave the HW and CH working as normal. The other rads are still working. You'll need to repressurise when you refit the rad and bleed it as it refills.
But why bother removing the rad? It's usually possible to paint or wallpaper behind a rad so the bits missed aren't readily visible.
its a towel rad . he could hide the missing bits with a towel ;)
 
If you isolate one rad you can leave the HW and CH working as normal. The other rads are still working. You'll need to repressurise when you refit the rad and bleed it as it refills.
But why bother removing the rad? It's usually possible to paint or wallpaper behind a rad so the bits missed aren't readily visible.
Not on a towel rail
 
No water coming out. What best course of action, only need to drain upstairs towel rail.
I was thinking flexible bucket & drain the raid. OR remove a d/stairs rad & drain from there.
I want EASY please.
What would plumbers do.
edit
I have opened a bleed valve
 

Attachments

  • plumb.jpg
    plumb.jpg
    125.1 KB · Views: 33
Towel rads are notoriously difficult to drain if the valves are stright and the pipework is down into the floor. Not so much if the valves are right angled into the wall. Which are yours?

Draining rads I then I use a plumb tub.

1743871888296.png
 
Close both towel rail valves.
Crack one of the nuts from rail to valve.
Have a baking tray or hole less rubble bag around the rad tail.
Open air vent and control flow of water into recepticle by opening and closing the air vent.
When it's empty close air vent and remove rail.
 