Is it OK to have hot water with a drained sealed system?

Joined
23 Apr 2009
Messages
45
Reaction score
2
Location
Argyll
Country
United Kingdom
I'm planning on replacing all the old radiators in my house. I have a combi boiler and was wondering, as it might take a couple of days, is it OK to drain the central heating system but leave the boiler on so we can have hot water? Obviously I'd turn the boiler to 'water only'.
 
Sponsored Links
you could but it's not advisable

1 after hot water demand the boiler dumps residual heat into the heating system

if it has nowhere to go the boiler will overheat

2 if you close the isolater valves under the boiler they will probably start to leak

:cry:
 
No, you need a htg circuit to pressurise the boiler.

You could connect a coil of plastic pic as a temp, but hardly seems worth the effort.
 
It all depends on which boiler you have.

I would say that with virtually ALL boilers you can pressurise it and use it for hot water only while you change your rads.

In spite of what the others say I do it regularly and have never had any problems.

I have seen several Biasis and a Performa used as a hot water unit with no rads connected. On one the installer had connected a pipe between the flow and return, the others were capped off. BUT these boilers have a built in bypass.

If your boiler has a built in bypass then I would say just do it.

If you are not sure, or it has not, then temporarily looping the flow and return together.

Tony
 
Sponsored Links
And how much would a new boiler in Argyle cost if it all goes tits up.
 
agile said:
I have seen several Biasis and a Performa used as a hot water unit with no rads connected. On one the installer had connected a pipe between the flow and return, the others were capped off. BUT these boilers have a built in bypass.

can't see what difference a built in bypass will make at best 150mm of 8mm tube
 
It enables a flow through the heat exchanger to prevent it overheating as a result of the latent heat contained in it following a demand for DHW..

Tony
 
It increases the water in the boiler from about 65° to say 85°.

Tony
 
Thanks everyone for your help. Think I'll err on the side of caution and leave it off.
 
If you look in the MI it will tell you whether it can or can't.

Post the make/model and we will know as well.
 