combi timer switch replacement

Joined
9 Feb 2005
Messages
16
Reaction score
0
Country
United Kingdom
Hi there, I have what basically is a light switch wired into my combi boiler, so i can just switch on and off without going up to loft to do it,

Now i have bought a centaurplus c17 timeswitch and was hoping to just replace the light switch with this programmer, however when i connected it up it wouldn't let me control boiler at all, it was just staying on,

the cable has only a live and neutral wire on it going to lightswitch and i thought the new timeswitch would do the exact same on, off etc,

what do i need to make the programmer work?

cheers in advance
 
Sponsored Links
Without more details, it's difficult to be sure but I would imagine that the "live" and "neutral" you refer to are actually a live, and a switched live. If so, there is no neutral which you will need to operate a timeswitch.

If my assumptions are correct, then:

Connect the live to [L]
Connect the switched live to [4]
Run a neutral wire from the boiler N to the programmer [N]
You will also need to link [L] and [2]
 
Sponsored Links
Thanks for reply, what details do you need?
The boiler details would be good, and I see you've done that. Thank you. It would be helpful to know where the two wires you have assumed are live and neutral are connected at the other end. Assuming that they are both connected to the boiler, a photograph of the connections would be really useful too.
 
Thanks for reply, what details do you need?
The boiler details would be good, and I see you've done that. Thank you. It would be helpful to know where the two wires you have assumed are live and neutral are connected at the other end. Assuming that they are both connected to the boiler, a photograph of the connections would be really useful too.


Ok will get pic together and get back to u, really appreciate it thanks
 
firstly it's never a live and neutral to a light switch, it's a live and a switched live return..

you need a battery operated controller as you don't have a neutral there, or change the cable to a 3 core + earth.
 
firstly it's never a live and neutral to a light switch, it's a live and a switched live return..

you need a battery operated controller as you don't have a neutral there, or change the cable to a 3 core + earth.


Ok so i replace the cable to 4 core and connect to neutral, live and switched live on boiler then connect to relevant ones on controller yeah?

i take it when i look at boiler i will see a neutral connection there next to the 2 that is connected already?
 