88% efficient, even when it is not condensing. This rises to about 92% when it is condensing
A bit better than that I'm sure - sedbuk is about
seasonal efficiency - like an
urban cycle rather than comparing specific speeds. Correct me if I'm wrong.
Sedbuk efficiency is calculated from two figures: The full load efficiency and the part load (30%) efficiency. Full load is measure with the boiler running at 80°C/60°C - so well above the condensing temperature. Part load is measured at 50°C/30°C. Take the Baxi Solo HE A 18 as an example:
At 80/60 the input is 20.18kW and the output 17.81kW, giving an efficiency of 88.25%. At 50/30 the output is 19.27KW, giving an efficiency of 95.5%
Another thing to be aware of is that some manufacturers, particularly continental, use net efficiency not gross. (The Baxi example above is gross.) Net efficiencies produce efficiency figures of above 100% at part load. For example the Greenstar 40cdi Regular:
At 80/60 the input is 42kW and the net output is 40.8kW, giving a net efficiency of 97.1%. At 50/30 the net output is 43.3kW, giving a net efficiency of 103%.
Furthermore, the way Sedbuk efficiencies have been calculated has changed, so the A-G gradings have been dropped. The database just shows the (new) SAP2009 Annual efficiency and the (old) SAP2005 Seasonal efficiency, which was the basis for the A-G grades. The new efficiencies are lower than the old. You can read an explanation on the Sedbuk website.
The whole weather compensation issue is a mess at the moment. Companies like Viessmann are making silly claims like 20%
I agree that the WC issue is a mess - in the UK that is, but can't comment on Viessmann's claims
Yes boilers modulate themselves down - some can go further than others.
If you set the boiler max temp yourself to say 75º, it'll be condensing (when the return is below about 56). You can do that for all but the coldest weather. A WC boiler would be running at a lower temp than that for longer, but the savings are small and really unknown.
The main difference between a WC boiler and a non-WC boiler is that the non-WC boiler will modulate to maintain a
constant flow temperature while the WC boiler modulates to maintain the
appropriate flow temperature for the weather conditions. The modulation of a non-WC boiler is effectively nothing more than a fancy way of range-rating the boiler. A non-WC boiler will tend to cycle more.