Cuitting channels into concrete slab for plumbing and electrics

Discussion in 'Plumbing and Central Heating' started by DerMitchie, 2 Feb 2021.

  1. DerMitchie

    DerMitchie

    Joined:
    22 Jan 2021
    Messages:
    17
    Thanks Received:
    0
    Country:
    United Kingdom
    We are having to cut out channels in our existing kitchen floor slab for a new kitchen island.

    I will need to place an electric feed for the sockets; cold feed, hot feed and a gas pipe. I will also have to re-do some drainage so will dig out for that and re-cover.

    So I guess I'm keen on tips/suggestions with regards to

    1. depth of channel(s)
    2. Plumbing: can I bury pushfit/speedfit type plastic pipes/connectors in concrete for hot/cold - do they need to be lagged/insulated?
    3. Gas: The plumber will place that pipe and connect etc. Any advice?
    4. Electrics: What type of ducting should I use, if any? It's just one ring main.
    5. Screed: What mix/material should I use?
    6. DPM - is this required? Not sure if one is there as it's an old extension.
     
  2. Sponsored Links
  3. sxturbo

    sxturbo

    Joined:
    12 Jan 2014
    Messages:
    3,166
    Thanks Received:
    466
    Location:
    Essex
    Country:
    United Kingdom
    1. depth of channel(s) - whatever depth you need
    2. Plumbing: can I bury pushfit/speedfit type plastic pipes/connectors in concrete for hot/cold - do they need to be lagged/insulated? copper, and lagged
    3. Gas: The plumber will place that pipe and connect etc. Any advice? make sure the calcs are done correctly to determine pipe diameter from gas meter, it may require upgrading to 28mm

    6. DPM - is this required? Not sure if one is there as it's an old extension. my house was built in early 70's and has dpm, so i imagine it will, whatever you damage you must replace
     
  4. DerMitchie

    DerMitchie

    Joined:
    22 Jan 2021
    Messages:
    17
    Thanks Received:
    0
    Country:
    United Kingdom
    Just out of interest, why Copper and not plastic? In my previous property the builder used plastic.
     