So I know the Pyronix Enforcer v11 panel supports a number of wired expansion devices such as wired keypads and the Euro ZEM8/ZEM8+ input expanders using the RS485 protocol.

My question is how much electrical current can the Enforcer V11 handle? Is it 500mA as given by the fuse or less than that?

For example, could the Enforcer v11 panel handle 3 x of the wired Euro Surface mount Key pad's and the Euro ZEM8/ZEM8+ input expander feeding 8 wired PIR's for example or not?

Maybe for a fully wired system, something like the Euro 76 would be better?

Regards: Elliott.
 
Handle, or draw from it.

You can’t exceed the fuse and you may want to allow a buffer of 5-10%.

Like most things if the power available is going to be exceeded external power supplies maybe used
 