I'm not sure what you mean by a 'dedicated appliance', but if you're talking about an appliance protected by a 13A fuse (in a plug or fused connection unit), then you need at least 1.25mm² flex, usually 1.5mm². Whether or not it needs to be heat-resistant flex depends upon exactly what the appliance is, and where the flex will be sited.What flex should be put on a 13amp dedicated appliance?
What's a dedicated appliance?
You may be right, but it's also possible that Granny left first!Bet it left in the end, though.![]()
The size and type of cable stated by the manufacturer.
At a 13amp load, 1.5mm² may be OK if the cable length is relatively short. Longer lengths of cable run, or cables in warm environments may mean a larger csa is needed.
Would that be marked CE ?0r a 0.25 mm² flex on China Export?
Fair enough but can you be certain?Now come on lads the BS7671:2008 is the one which refers to dedicated supply and saying appliance instead of supply is clearly just a slip up.
It could be protected by a BS3036 and require derating.Table 4F3A states 1.25 mm² for 13A single phase a.c. for flexible cord.
I know you find lead sets with 10A IEC sockets and 13A Plugs with 0.75mm² cable but that does not mean it's allowed. Even 10A requires 1 mm² cable and I think the moulded plug and socket leads with 0.75 mm² cable are designed as computer supplies and not kettle supply. I know the notch is normally found with the kettle (C15 - C16) which will take the higher temperature but the (C13 - C4) IEC lead is still rated 10A as is the (C15 - C16) non of them are rated at 13A so should only be used up to 2.3kW however since a kettle boils in just a few minutes there is not really a problem with such a short time of overload.The size and type of cable stated by the manufacturer.
Or a 0.75mm^2 cable not exceeding 2m in length fitted with a moulded plug?
That sounds very reasonable.Towards the end of my career, I saw many (often brand new) appliances with 0.75 flex and moulded plugs, fitted with 13A fuses and, rightly or wrongly, I failed them when PAT testing or called them into question when coming across them on other jobs, simply because 0.75 did not equal 13A according to 7671.
I'm struggling a bitThis from an IEE thread:
.... So, 18W fridge freezer, 0.75 sq mm flex, 13A fuse, is quite safe and acceptable provided the flex length is below the limit in Table 2 of BS1363-1.