Hello all,
Before cracking into my lighting circuits (tacking a few things on up & downstairs) I've been doing some checks beforehand like a good boy scout. First up was insulation and I've come a cropper
Earthing is TN-C-S and the meter is a Fluke 1587FC. Measuring per instructions in OSG & GN3 with only the breaker for the circuit in question closed - all other switches open (including all the 2way switches in the rooms)
[email protected] (unless in brackets, in which case it's just on normal ohm range for info)
Downstairs
---L/N = 0 Mohm (680kohm)
---L/cpc = >275 Mohm
---N/cpc = 0.4 Mohm
Upstairs
---L/N = 0 Mohm (1.2Mohm)
---L/cpc = 0.4 Mohm
---N/cpc = 0.4 Mohm
I'm hypothesizing that a cable got crushed upstairs and a borrowed neutral too (stairway up/down switches wiring is a bit of a joke), but I have not much experience diagnosing this sort of thing. Borrowed Neutral plausible for sure but the crushing idea seems pretty infeasible, squished *just enough* to destroy the isolation but not enough to keep blowing the RCD? I don't think I'm right...
Does this smack of anything in particular to you knowledgeable folks out there?
There *are* dimmers upstairs, but none downstairs...(although god knows one might've been plastered into a wall in the past knowing this place...)
Hmm I guess next step is tie the L and N and test to cpc?
I could get hold of a capacitance meter I guess to check for power electronics on the bus but not until Monday and I was really hoping to get my new stuff hooked up...
Any ideas welcome! Thanks in advance
Al
Before cracking into my lighting circuits (tacking a few things on up & downstairs) I've been doing some checks beforehand like a good boy scout. First up was insulation and I've come a cropper
Earthing is TN-C-S and the meter is a Fluke 1587FC. Measuring per instructions in OSG & GN3 with only the breaker for the circuit in question closed - all other switches open (including all the 2way switches in the rooms)
[email protected] (unless in brackets, in which case it's just on normal ohm range for info)
Downstairs
---L/N = 0 Mohm (680kohm)
---L/cpc = >275 Mohm
---N/cpc = 0.4 Mohm
Upstairs
---L/N = 0 Mohm (1.2Mohm)
---L/cpc = 0.4 Mohm
---N/cpc = 0.4 Mohm
I'm hypothesizing that a cable got crushed upstairs and a borrowed neutral too (stairway up/down switches wiring is a bit of a joke), but I have not much experience diagnosing this sort of thing. Borrowed Neutral plausible for sure but the crushing idea seems pretty infeasible, squished *just enough* to destroy the isolation but not enough to keep blowing the RCD? I don't think I'm right...
Does this smack of anything in particular to you knowledgeable folks out there?
There *are* dimmers upstairs, but none downstairs...(although god knows one might've been plastered into a wall in the past knowing this place...)
Hmm I guess next step is tie the L and N and test to cpc?
I could get hold of a capacitance meter I guess to check for power electronics on the bus but not until Monday and I was really hoping to get my new stuff hooked up...
Any ideas welcome! Thanks in advance
Al