The extension cable presumably has a 13A BS1362 fuse, and that is deemed to be adequate to protect a 1.5mm² cable..... but I have been seeing very long 13A extension cables and (very long) temporary installations sometimes in 1.5mm cable with C16 overcurrent protection ...
What do you mean by the "minimum permitted Ze", since, if you actually mean Ze, there is surely no such thing? If you are talking about fault loop impedance (L-E or L-N) then, for a given OPD, there is surely a 'permitted maximum', not minimum?Yes that's what I'm measuring the L-N loop impedance/PSSC (tester shows both at the same time). Sometimes it's higher than the minimum permitted Ze ...
Indeed not - but, as I said before, that formula is only valid when adiabatic conditions apply - i.e. only for short disconnection times, certainly no greater than 5 sec. That's why Table 43.1 only gives values of 'k' for disconnection times up to 5 sec.Yes that's another way to write t = (k2*S2)/I2 I have both in the excel sheet I have been playing around with. It doesn't help with calculating disconnection time from fault current/loop impedance.
Kind Regards, John