Are there formulae to calculate fuse/mcb disconnection times at a given fault current instead of having to look up graphs? The same question as being asked here: https://electronics.stackexchange.c...ermine-a-formula-for-fuse-disconnection-times
I don't know for certain, but I doubt it, because I think the graphs we see are almost certainly empirically-based, rather than based on theory. One could (approximately) mathematically model those empirical curves and thereby produce 'formulae', but those formulae might well be complicated and would quite probably be completely different for each rating of MCB/fuse, so it probably would not be worthwhile to create them.Are there formulae to calculate fuse/mcb disconnection times at a given fault current instead of having to look up graphs? The same question as being asked here: https://electronics.stackexchange.c...ermine-a-formula-for-fuse-disconnection-times
No.Are there formulae to calculate fuse/mcb disconnection times at a given fault current instead of having to look up graphs?
If that is really what they meant, it is entirely the wrong process - fuse ratings and type are not selected based on the disconnection time.https://electronics.stackexchange.com/questions/129632/can-i-determine-a-formula-for-fuse-disconnection-times said:I'm currently updating an electrical design process where currently, the designer needs to manually refer to the graph to see which fuse should be used.
Even the log-log graphs we are used to seeing are far from linear (other than for some types of fuses - but even they are certainly not truly linear). Any continuous curve without discontinuities can theoretically be modelled (to create a formula), so that could be done for a particular type/rating of fuse or the thermal part of the curve for an MCB of a particular type/rating, but, as I said, the resulting formulae could be very complex and would probably be different for every device/rating.If it's a linear gradient graph it sold be reasonably easy, I would hazard a guess they are none linear though at certain points.
Quite so - and much simpler.Plus a proven graph by testing/ retesting is more reliable imho.
I still don't really understand. If you are talking about 'fault current' in the correct sense (i.e. a 'short circuit'), then the Zs at the furthest point in the circuit will determine the magnitude of the fault current, and the specification of the OPD will then indicate whether that fault current is enough to produce the required 'immediate detection' - e.g. with a Type B MCB, since it's magnetic tripping has to happen between 3 and 5 times its rating (In), one has to assume that it could take 5 times In (e.g. 160A for a B32 MCB).Not every installation has been designed though, some have just been chucked together! And when assessing existing installations and temporary installations it would be useful to know whether the fault current would be sufficient to operate the cpd before the cable overheated, for example (at the end of a 80m extension cable from a submain perhaps!).
As above, I'm still not clear what you are trying to achieve, but you give a little insight when you go on to say ...I'm just trying to make up some formulae in Excel and this is leaving a hole.
You now seem to be talking about a non-complaint circuit, with an excessive Zs. The required disconnection times are related to safety (primarily protection against electric shock), rather than overheating of the cable. Even if you did determine (from graphs, or a formula if it existed) the time that it would take for a (true) fault current to operate the OPD, given that the fault current was too low for the required 'immediate' disconnection, I don't really know how that information would really help you. What do you think it would tell you, other than that the circuit was non-compliant and therefore not deemed to be 'safe'?I can derive how long a cable will take to overheat from the fault current but not how long it will take to operate a given cpd. I can tell the client that a fault won't disconnect within the required time, but I can't tell them how long it will take. I guess due to the nature of the devices it's not simple to calculate and would be likely to be inaccurate in real life scenarios anyway.
You mean Zx? Yes, I was wondering if there's a formula for Zx/disconnection time if you prefer that to fault current/disconnection time.I still don't really understand. If you are talking about 'fault current' in the correct sense (i.e. a 'short circuit'), then the Zs at the furthest point in the circuit will determine the magnitude of the fault current
So what's the disconnection time if the fault current is 127A as I recently measured at the end of a long extension, and would that trip the breaker or blow the 13A fuse first?and the specification of the OPD will then indicate whether that fault current is enough to produce the required 'immediate detection' - e.g. with a Type B MCB, since it's magnetic tripping has to happen between 3 and 5 times its rating (In), one has to assume that it could take 5 times In (e.g. 160A for a B32 MCB).
I'm not talking about overload currents, that's an easy one, check the CCC of the cable in the installed conditions... done.As for 'overload' currents, that's just a question whether (as required) all cables (including any flexible extensions!) have a CCC which is no less than the In of the OPD. If that is satisfied, then the cable is regarded as adequately protected from overheating. Length of cables is not a consideration in that respect.
It would tell me how long it would take to disconnect the fault, which I could then explain to the client instead of saying, "it won't trip fast enough, but I don't know how long it will take to trip".Even if you did determine (from graphs, or a formula if it existed) the time that it would take for a (true) fault current to operate the OPD, given that the fault current was too low for the required 'immediate' disconnection, I don't really know how that information would really help you. What do you think it would tell you, other than that the circuit was non-compliant and therefore not deemed to be 'safe'?
I could create look-up tables in excel, that would be a pain and so I was wondering if there were formulae. Have you never wondered how long a non-compliant circuit would take to trip? Or how that compares with the maximum time to reach the cable limiting temperature (434.5.2...)?In any event, as has been said, it would be impractical to derive 'formulae'. If there was some perceived point in the exercise (estimating actual, non-compliant, disconnection times) you could do it in software by creating look-up tables containing data read from the published graphs (probably different for each type and rating of OPD), extrapolating between points in that look-up data if you wanted to - but I still don't see what that would achieve.
No, I meant what I typed - Zs. Zx is (in BS7671) the impedance of a floor!You mean Zx?
If there were a formula in terms of Zs, it would be trivial to re-write it in terms of fault current, since fault current = 230/Zs. However, as you've been told, there is no such formula.Yes, I was wondering if there's a formula for Zx/disconnection time if you prefer that to fault current/disconnection time.
Given that 127A is so many times the In of the 13A fuse, that would blow virtually instantly, even if the breaker did not operate first. How long the breaker would take would, obviously, depend upon its rating. If it were a B32 then, per graphs, it could take about 20 seconds - but the fuse would probably have blown long before that had a chance to happen..So what's the disconnection time if the fault current is 127A as I recently measured at the end of a long extension, and would that trip the breaker or blow the 13A fuse first?
You could - but I don't know what either you or the client could usefully do with that information.It would tell me how long it would take to disconnect the fault, which I could then explain to the client instead of saying, "it won't trip fast enough, but I don't know how long it will take to trip".
As you've been told, there aren't formulae.I could create look-up tables in excel, that would be a pain and so I was wondering if there were formulae.
Yes, on occasions I have wondered that - and, when I have, I've looked at the graphs.Have you never wondered how long a non-compliant circuit would take to trip?
How exactly would you determine that?Or how that compares with the maximum time to reach the cable limiting temperature (434.5.2...)?
Well Zs is the earth loop impedance and for the purposes of my enquiry that's not relevant, I'm looking at L-N faults.No, I meant what I typed - Zs. Zx is (in BS7671) the impedance of a floor!
If there were a formula in terms of Zs, it would be trivial to re-write it in terms of fault current, since fault current = 230/Zs. However, as you've been told, there is no such formula.
Quite, but 127A was just an example, and virtually instantly is not a time that may or may not be less than 0.4s for exampleGiven that 127A is so many times the In of the 13A fuse, that would blow virtually instantly, even if the breaker did not operate first. How long the breaker would take would, obviously, depend upon its rating. If it were a B32 then, per graphs, it could take about 20 seconds - but the fuse would probably have blown long before that had a chance to happen..
That's OK John you don't need to know everything.You could - but I don't know what either you or the client could usefully do with that information.
Yeah that's why I "was" wondering rather than "am" although you seem more certain than in your first reply.As you've been told, there aren't formulae.
Well for temperature rise you would use the formula t = (k2*S2)/I2 (nice and easy in excel), then you could compare that with the actual disconnection time, if you could calculate that.How exactly would you determine that?
Yes, it would be a bit of a pain - but, as has been said, I'm not sure you would have any alternatives.I could create look-up tables in excel, that would be a pain and so I was wondering if there were formulae.
Yes, it is; That's virtually all that matters.Well Zs is the earth loop impedance and for the purposes of my enquiry that's not relevant,
Then measure the Neutral loop.I'm looking at L-N faults.
I don't know if John meant to say "virtually"; instantaneous is 0.1s but the maximum Zs for 1362 fuses is for 0.4s which is all that is required.Quite, but 127A was just an example, and virtually instantly is not a time that may or may not be less than 0.4s for example
You could use s=[sq.rt.((I sq.) x t)] / k. If it is large enough then all is well - but for that you have to use a graph to find the time.Well for temperature rise you would use the formula t = (k2*S2)/I2 (nice and easy in excel), then you could compare that with the actual disconnection time, if you could calculate that.
I'm not sure why you want to ignore the possibility of L-Well Zs is the earth loop impedance and for the purposes of my enquiry that's not relevant, I'm looking at L-N faults.
With 127A through a 13A BS1362, "virtually instantly" would be an awful lot less than 0.4s - seemingly something around 0.005s according to the curves I have.Quite, but 127A was just an example, and virtually instantly is not a time that may or may not be less than 0.4s for example
When I wrote my firts reply, I was certain that there would/could be no (accurate) theory-based formulae. As I said, it would be possible to mathematically model the empirical curves and, although I was not certain, I found it hard to believe that anyone would have bothered to do that - particular because I don't believe that there would be any generally-perceived 'need' (even if you have one).Yeah that's why I "was" wondering rather than "am" although you seem more certain than in your first reply.
That is a re-arrangement of an adiabatic equation, and hence is only valid if adiabatic conditions apply (i.e. if the disconnection time is less than about 5s) - and I thought the whole point of what you seem to be trying to do was to determine disconnection times which could well be quite prolonged? In any event, even for disconnection times ≤5s, it would not tell you what the temp rise was - merely whether or not it was regarded as 'safe'.Well for temperature rise you would use the formula t = (k2*S2)/I2 (nice and easy in excel), then you could compare that with the actual disconnection time, if you could calculate that.
Zs can be many even hundreds of ohms if the circuit is RCD-protected but large L-N loop impedances (what I was calling Zx) mean low short circuit fault currents which means longer disconnection times and possible melting cables (you get 4-way adapters with 1mm cable for example). In a properly designed circuit volt drop limits mean you never get near that point but I have been seeing very long 13A extension cables and (very long) temporary installations sometimes in 1.5mm cable with C16 overcurrent protection. Even if the cable isn't going to melt I would still like to know approximately how long a fault will take to clear (without have to get the book out).Yes, it is; That's virtually all that matters.
If that complies then all is well.
Yes that's what I'm measuring the L-N loop impedance/PSSC (tester shows both at the same time). Sometimes it's higher than the maximum permitted Zs, automatic disconnection has to come before the cable overheats (343.5.2). You have to check the graphs/tables.Then measure the Neutral loop.
It will nearly always be 'better' than L-E.
Yes that's another way to write t = (k2*S2)/I2 I have both in the excel sheet I have been playing around with. It doesn't help with calculating disconnection time from fault current/loop impedance.You could use s=[sq.rt.((I sq.) x t)] / k. If it is large enough then all is well - but for that you have to use a graph to find the time.