What benefit derives from 'earthing something which is supplied with ELV?..... PELV (An extra-low voltage system which is not electrically separated from Earth, but which otherwise satisfies all the requirements for SELV.) so with a PELV there should be an earth.
Why there are three ELV I can only read BS7671 where SELV, PELV and FELV are defined. I would guess it is where low voltage can in some way connected to the ELV.What benefit derives from 'earthing something which is supplied with ELV?
Kind Regards, John
Your LED "driver" has Line and Neutral input terminals which connect to the UK (Nominal) 230 V AC (50 Hz) Supply.Do 24v led strips need to be earthed? My led driver only has Live and Neutral terminals.
Firstly, I think there is a risk that two aspects of "earthed" may be getting confused. The BS7671 definitions of PELV and SELV relate to whether or not the supply/system is earth-referenced - i.e whether or not one side of the supply (or some point intermediate between the two sides) is connected to earth. The question we seem to be addressing in this thread is whether components of an ELV system (e.g. exposed-conductive parts) need to be earthed as a measure to reduce the risk of electric shock - and (so long as LV is not also 'involved') #earthing' (e.g. of exposed-c-ps) is irrelevant in the case of SELV, since it is not an earth-referenced supply. With PELV, earthing of exposed-c-ps will only reduce the risk of ('small', ELV) electric shocks if the ELV supply has adequate fault protection.Why there are three ELV I can only read BS7671 where SELV, PELV and FELV are defined. .....
... are straightforward enough. They are essentially the same as one another, other than that a PELV supply/system is earth-referenced, whereas SELV is not. This distinction says nothing about the need (or not) for 'protective earthing' - other than, as above, it would be useless for that purpose with SELV.SELV (separated extra-low voltage). An extra-low voltage system which is electrically separated from Earth and
from other systems in such a way that a single fault cannot give rise to the risk of electric shock.
PELV (protective extra-low voltage). An extra-low voltage system which is not electrically separated from Earth,
but which otherwise satisfies all the requirements for SELV.
... and I am struggling to understand what it means, or what situations would qualify as 'FELV" by this definition. Since the definition is silent as to whether the supply is or is not earth-referenced, that seems to imply that the only way something can be "FELV" is if it is NOT "separated from other systems in such a way that a single fault cannot give rise to thee risk of electric shock" - which makes no real sense to me!Functional extra-low voltage (FELV). An extra-low voltage system in which not all of the protective measures
required for SELV or PELV have been applied.
Well, yes, that's the nearest to an explanation which makes at least some sense, but I'm not convinced that it's necessarily a lot of sense - not the least because a comparable argument could sometimes exist with LV as well as ELV (e.g. in the case of an 'isolating transformer' with a floating output)..... I would guess it is where low voltage can in some way connected to the ELV.
Why not? RCDs only know about current, and have no idea what voltages exist in the circuit. Standard RCDs would, of course, not work with DC, and a lot of ELV is DC, but, as you know, BS7671's requirements for RCD protection specifically only relate to 'AC systems'.I noted when the rules on RCD use came out in 2008 it did not state for low voltage only, clearly would not work with ELV ...