Hi all
I recently had an electrician round to do some electrical work and he had to go inside the airing cupboard terminal box as he used some old wiring for our unused thermostat (we got a Tado last year)
I believe he’s snipped something he shouldn’t as motor is not getting any power at al, tested with voltage pen. It’s currently stuck on HW only (can set to manual)
I have a PMV22 Salus.
The white wire goes into my terminal box with nothing coming out of it and it never goes live (manual says it should be live with HW is on)
I have a unused live wire from the stat that goes live when HW is on (I assume this is to power the white wire?).
electrician saying they only cut the wire for the old stat but clearly they’ve done something else...may need to charge me.
does it sound like my loose live wire ought to be plugged into the terminal against the white wire?