Thinking of having a new cooker (range sort of thhing) and may want to go for duel fuel. At present my cooker is gas only so understand this would mean running a new cable 6mm2 (most likely from the CU) to the cooker.
I have one spare way in my CU (at the end after the 6A mcb for my downstairs lights. As the cooker circuit would be a high value MCB (40A) can it just be 'plugged' in that spare way or should they all be moved along.
Just tryng to judge if it's worth it in terms of getting a spark in if its too much work then I think I will do more digging and perhaps just go for a gas only range (though I think dual fuel is better for making cakes - apparently - so the missus says!!).
Thanks in advance