We have items which heat the house, which in winter is not a problem, but in summer is. So we have tried to reduce the heat output of equipment as much as possible, so our lights, TV, and many more items are today using switch mode power supplies and vastly reduce the power used in the home.
There are items which do draw more, like charging an electric car. But we are looking at the loading of circuits within the home, not the total that the home uses. My parents, my first, and second house, all had Wylex fuse boxes with 4 fuses. Cooker, Ring final, immersion heater, lights. Today my home has 14 RCBOs plus an UPS circuit still with a 60 amps incoming fuse, so 8 circuits feed 13 amp sockets, until now never counted them, but 2 feed outside sockets, 2 also feed cookers, 1 is the ups, remaining 3 ring finals.
We have no idea on how many circuits @DIYjobber intends to spread the load over. And with a ring final, how close the heat pump load would be to the centre of the ring. We are told the load is 1.56 kW which should not really be a problem. In summer, I use a portable AC, which I never even considered would need a dedicated supply for.
However, if I wanted a heat pump, I would include the cost to modify my installation in the cost when selecting the device. The same as any other household appliance, be it an oven, hob, shower, or heat pump, one has to include installation in the price, if to change my electric shower one model would require heavier cable to be drawn in, I would include that cost when selecting the shower.
There are items which do draw more, like charging an electric car. But we are looking at the loading of circuits within the home, not the total that the home uses. My parents, my first, and second house, all had Wylex fuse boxes with 4 fuses. Cooker, Ring final, immersion heater, lights. Today my home has 14 RCBOs plus an UPS circuit still with a 60 amps incoming fuse, so 8 circuits feed 13 amp sockets, until now never counted them, but 2 feed outside sockets, 2 also feed cookers, 1 is the ups, remaining 3 ring finals.
We have no idea on how many circuits @DIYjobber intends to spread the load over. And with a ring final, how close the heat pump load would be to the centre of the ring. We are told the load is 1.56 kW which should not really be a problem. In summer, I use a portable AC, which I never even considered would need a dedicated supply for.
However, if I wanted a heat pump, I would include the cost to modify my installation in the cost when selecting the device. The same as any other household appliance, be it an oven, hob, shower, or heat pump, one has to include installation in the price, if to change my electric shower one model would require heavier cable to be drawn in, I would include that cost when selecting the shower.