Double socket earth connection

So are you saying take faceplate off again & check whats fitted / put photo here ?

If its metal then add an extra earth BUT if not leave as is.

Please advise Thanks
I would, but then you'll need a short length of 2.5mm plus some earth sleeving. At a push, you could remove the earth wire from a scrap piece of 2.5mm flex and use that.
 
Ok
I remembered that I took a photo of the wiring before I changed anything.
Photo supplied.

Sounds like I need to add an earth as I see it’s metal BUT from photo I don’t see if there’s a screw fitting to accept the wire so will pop it off again & look.

Let’s assume there is no screw to accept the new earth & after screwing it back up my tester doesn’t go beep on the two screws then it’s not live & just leave it at that.
 

Attachments

  • IMG_4530.jpeg
    IMG_4530.jpeg
    647.3 KB · Views: 18
So the outcome is & remember I said at the start I’ve never seen two earths.

Well the other earth does go to a screw in the metal back box.

So I’m now all sorted.
 

Attachments

  • IMG_4532.jpeg
    IMG_4532.jpeg
    782.5 KB · Views: 19
So the outcome is & remember I said at the start I’ve never seen two earths.

Well the other earth does go to a screw in the metal back box.

So I’m now all sorted.
Some people rely on the screws to bond the faceplate to the box.

Of course, that stops working when you take the screws out, perhaps for repair or decorating.

Very rarely, in damp conditions, the lugs get rusty enough to lose continuity, and, in damp fault conditions, there can be a shock risk.

A pigtail gives you belt and braces.

I did once consider going into business selling 100mm flexible pigtails for a pound each.
 
As a decorator, I would rather that all metal back boxes were earthed. I have lost count of the times that a live popped out as I loosened the socket faceplate so that I could paper behind it.

Frankly, I consider the lack of an earth to the metal back box as a sign of laziness.
 
I don't see why it should be better.
As I understand it, the 2 earthing points are used for 2 independent rings of CPC in high integrity circuits to reduce the possibility of losing an earth. There was once a very many page discussion on the subject involving at least one forum member who decided some time later to stop visiting.
Thanks
So im not all sorted
I think you are. In my opinion:
- The original electrician should have sleeved the two ring earths separately.
- He should not have cut the outer sleeving back so tightly.

However I wouldn't bother about it now.
 
As I understand it, the 2 earthing points are used for 2 independent rings of CPC in high integrity circuits to reduce the possibility of losing an earth.
Yes, that's what BS7671 implies.

If if is intended for two "separate" earths it makes more sense.
Not really.

'high integrity' earthing is used for socket outlets for circuits which have more than 10mA of protective conductor current.
At the same time, all socket outlets require additional protection from 30mA RCDs.
The maximum protective conductor current for a 30mA RCD to avoid nuisance tripping is 30%, or 9mA.

The 'high integrity' regulations in BS7671 all end in 201/202/203 and so on which identifies them as UK only items that have been added in for unspecified reasons.
They should be deleted, just like most of the other UK specific junk.
 