Double socket earth connection

Here is a scenario to consider. One of the live wires chafes (ie no grommet used) and makes contact with the metal back box or plate screw (I have often seen faceplate screws that have gone through conductors because the wires weren't pushed neatly into the back box).

You have a plastic socket but the now live back box conducts through the two screws so you have two live metal screws on the plastic faceplate of your socket waiting to bite the unwary. This is the reason you should put another wire from the plate to the back box if it's metal. It doesn't matter what others have done in the past, two wrongs don't make a right as Mum used to say.

Can't tell from your photo if it's a metal back box or not. Which is why you should look at the box when doing this job.
I do not recall seeing a plastic socket that does not have the earth bar extending to brass surrounds around the screw holes, therefore providing the faceplates earthed, and the screws tight, the aboves unlikely
Saying that i opt to earth the backbox regardless ,often returning to the van to get a stupid bit of cable to do so
 
As a decorator, I would rather that all metal back boxes were earthed. I have lost count of the times that a live popped out as I loosened the socket faceplate so that I could paper behind it.

Yes, wires pop out. Why would separately earthing the back box help?

Frankly, I consider the lack of an earth to the metal back box as a sign of laziness.

Personally I put it somewhere on the spectrum of thing “often seen but not necessary”, to the left of earth wires connected to taps fed by plastic pipes but to the right of upgrading a CU to include RCDs.
 
both terminals are linked on the back of the faceplate anyway mate, it's just dual earth for high integrity circuits. you can pop one bare earth wire (sleeved in green/yellow obviously) into each terminal or shove both together into the same one if they fit cleanly, makes zero difference on a standard ring. just make sure you still run a little fly lead from one of the earth terminals into the metal back box lug so the casing is properly bonded.
 
Only where those sockets can never be used by persons of capability BA1, which is almost nowhere.
Almost, to quote Joe Lycett, doth butter no parsnips.

There are a few situations where an RCD can be omitted, which is what the RA is for.
 
I do not recall seeing a plastic socket that does not have the earth bar extending to brass surrounds around the screw holes,
They have existed, such as this 'HLM' branded effort.

hlm_socket.jpg
 
I don't have a copy of 1363; they are so prohibitively expensive.

I have bought BS1363 accessories with only one fixing hole having a connection to earth.
 